Re : désinstallation paquet ipp-linux impossible

On progresse sérieusement car ça démarre maintenant mais :

sudo upsdrvctl start
Network UPS Tools - UPS driver controller 2.7.1
Network UPS Tools - Generic HID driver 0.38 (2.7.1)
USB communication driver 0.32
Can't chdir to /var/run/nut: No such file or directory
Driver failed to start (exit status=1)
Network UPS Tools - Generic HID driver 0.38 (2.7.1)
USB communication driver 0.32
Can't chdir to /var/run/nut: No such file or directory
Driver failed to start (exit status=1)
Network UPS Tools - Generic HID driver 0.38 (2.7.1)
USB communication driver 0.32
Can't chdir to /var/run/nut: No such file or directory
Driver failed to start (exit status=1)

Ubuntu 22.04.3 sur portable et 23.10 sur fixe

Hors ligne

#27 Le 17/01/2016, à 23:58

nany

Re : désinstallation paquet ipp-linux impossible

Il faut créer le répertoire, lui mettre les propriétaires et les droits :

sudo mkdir /var/run/nut
sudo chown root:nut /var/run/nut
sudo chmod 770 /var/run/nut

EDIT : comme ça avance plutôt bien, donne le retour de

sudo cat /etc/nut/nut.conf

Dernière modification par nany (Le 18/01/2016, à 00:03)

En ligne

#28 Le 18/01/2016, à 00:07

jnq

Re : désinstallation paquet ipp-linux impossible

Voila lancement réussit ça tourne mais je perd l'indicateur graphique dans la barre de menu, il disparaît !

sudo upsdrvctl start
Mot de passe [sudo] pour moi : 
Network UPS Tools - UPS driver controller 2.7.1
Network UPS Tools - Generic HID driver 0.38 (2.7.1)
USB communication driver 0.32
Using subdriver: MGE HID 1.32

Dernière modification par jnq (Le 18/01/2016, à 00:08)


Ubuntu 22.04.3 sur portable et 23.10 sur fixe

Hors ligne

#29 Le 18/01/2016, à 00:09

jnq

Re : désinstallation paquet ipp-linux impossible

:~$ sudo cat /etc/nut/nut.conf
# Network UPS Tools: example nut.conf
#
##############################################################################
# General section
##############################################################################
# The MODE determines which part of the NUT is to be started, and which
# configuration files must be modified.
#
# This file try to standardize the various files being found in the field, like
# /etc/default/nut on Debian based systems, /etc/sysconfig/ups on RedHat based
# systems, ... Distribution's init script should source this file to see which
# component(s) has to be started.
#
# The values of MODE can be:
# - none: NUT is not configured, or use the Integrated Power Management, or use
#   some external system to startup NUT components. So nothing is to be started.
# - standalone: This mode address a local only configuration, with 1 UPS 
#   protecting the local system. This implies to start the 3 NUT layers (driver,
#   upsd and upsmon) and the matching configuration files. This mode can also
#   address UPS redundancy.
# - netserver: same as for the standalone configuration, but also need
#   some more network access controls (firewall, tcp-wrappers) and possibly a
#   specific LISTEN directive in upsd.conf.
#   Since this MODE is opened to the network, a special care should be applied
#   to security concerns.
# - netclient: this mode only requires upsmon.
#
# IMPORTANT NOTE:
#  This file is intended to be sourced by shell scripts.
#  You MUST NOT use spaces around the equal sign!

MODE=none

Le fichier est vide aucun instruction sauf mode none.

On arrête pour ce soir et aujourd’hui. Demain travail et neige  à rennes, ça va pas être triste. Rendez-vous demain soir après 17 h 30 au plus tôt.
Bonne nuit et encore merci. Bye

Dernière modification par jnq (Le 18/01/2016, à 00:12)


Ubuntu 22.04.3 sur portable et 23.10 sur fixe

Hors ligne

#30 Le 18/01/2016, à 02:22

nany

Re : désinstallation paquet ipp-linux impossible

Pas de problème. wink
Pour modifier nut.conf :

sudo sed -i 's/MODE=none/MODE=standalone/' /etc/nut/nut.conf

Ensuite, je souhaiterais voir ces trois autres fichiers :

cat /etc/nut/upsd.conf
cat /etc/nut/upsd.users
cat /etc/nut/upsmon.conf

D’ici là, je vais RTFM pour bien comprendre ce qu’il faut mettre.

En ligne

#31 Le 18/01/2016, à 05:56

moko138

Re : désinstallation paquet ipp-linux impossible

jnq a écrit :

Demain travail et neige  à rennes, ça va pas être triste.

Je croyais que le taf du Père Noël s'arrêtait le 25 décembre au soir ???


%NOINDEX%
Un utilitaire précieux : ncdu
Photo, mini-tutoriel :  À la découverte de dcraw

Hors ligne

#32 Le 18/01/2016, à 18:15

jnq

Re : désinstallation paquet ipp-linux impossible

Bonsoir, mode standalone en place. Je n'ai pas la permission de lire les fichiers demandés. L'indicateur graphique disparaît toujours au démarrage de la barre de menu.

upsd.conf non configuré :

# Network UPS Tools: example upsd configuration file
#
# This file contains access control data, you should keep it secure.
#
# It should only be readable by the user that upsd becomes.  See the FAQ.
#
# Each entry below provides usage and default value.

# =======================================================================
# MAXAGE <seconds>
# MAXAGE 15
#
# This defaults to 15 seconds.  After a UPS driver has stopped updating
# the data for this many seconds, upsd marks it stale and stops making
# that information available to clients.  After all, the only thing worse
# than no data is bad data.
#
# You should only use this if your driver has difficulties keeping
# the data fresh within the normal 15 second interval.  Watch the syslog
# for notifications from upsd about staleness.

# =======================================================================
# STATEPATH <path>
# STATEPATH /var/run/nut
#
# Tell upsd to look for the driver state sockets in 'path' rather
# than the default that was compiled into the program.

# =======================================================================
# LISTEN <address> [<port>]
# LISTEN 127.0.0.1 3493
# LISTEN ::1 3493
#
# This defaults to the localhost listening addresses and port 3493.
# In case of IP v4 or v6 disabled kernel, only the available one will be used.
#
# You may specify each interface you want upsd to listen on for connections,
# optionally with a port number.
#
# You may need this if you have multiple interfaces on your machine and
# you don't want upsd to listen to all interfaces (for instance on a
# firewall, you may not want to listen to the external interface).
#
# This will only be read at startup of upsd.  If you make changes here,
# you'll need to restart upsd, reload will have no effect.

# =======================================================================
# MAXCONN <connections>
# MAXCONN 1024
#
# This defaults to maximum number allowed on your system.  Each UPS, each
# LISTEN address and each client count as one connection.  If the server
# runs out of connections, it will no longer accept new incoming client
# connections.  Only set this if you know exactly what you're doing.

# =======================================================================
# CERTFILE <certificate file>
# CERTFILE /usr/local/ups/etc/upsd.pem
#
# When compiled with SSL support with OpenSSL backend,
# you can enter the certificate file here.
# The certificates must be in PEM format and must be sorted starting with
# the subject's certificate (server certificate), followed by intermediate
# CA certificates (if applicable_ and the highest level (root) CA. It should
# end with the server key. See 'docs/security.txt' or the Security chapter of
# NUT user manual for more information on the SSL support in NUT.
#
# See 'docs/security.txt' or the Security chapter of NUT user manual
# for more information on the SSL support in NUT.

# =======================================================================
# CERTPATH <certificate file or directory>
# CERTPATH /usr/local/ups/etc/cert/upsd
#
# When compiled with SSL support with NSS backend,
# you can enter the certificate path here.
# Certificates are stored in a dedicated database (splitted in 3 files).
# Specify the path of the database directory.
# 
# See 'docs/security.txt' or the Security chapter of NUT user manual
# for more information on the SSL support in NUT.

# =======================================================================
# CERTIDENT <certificate name> <database password>
# CERTIDENT "my nut server" "MyPasSw0rD"
#
# When compiled with SSL support with NSS backend,
# you can specify the certificate name to retrieve from database to
# authenticate itself and the password
# required to access certificate related private key.
# 
# See 'docs/security.txt' or the Security chapter of NUT user manual
# for more information on the SSL support in NUT.

# =======================================================================
# CERTREQUEST <certificate request level>
# CERTREQUEST REQUIRE
#
# When compiled with SSL support with NSS backend and client certificate
# validation (disabled by default, see 'docs/security.txt'),
# you can specify if upsd requests or requires client's' certificates.
# Possible values are :
#  - 0 to not request to clients to provide any certificate
#  - 1 to require to all clients a certificate
#  - 2 to require to all clients a valid certificate
# 
# See 'docs/security.txt' or the Security chapter of NUT user manual
# for more information on the SSL support in NUT.

Dernière modification par jnq (Le 18/01/2016, à 18:24)


Ubuntu 22.04.3 sur portable et 23.10 sur fixe

Hors ligne

#33 Le 18/01/2016, à 18:21

jnq

Re : désinstallation paquet ipp-linux impossible

upsd user non configuré :

# Network UPS Tools: Example upsd.users
#
# This file sets the permissions for upsd - the UPS network daemon.
# Users are defined here, are given passwords, and their privileges are
# controlled here too.  Since this file will contain passwords, keep it
# secure, with only enough permissions for upsd to read it.

# --------------------------------------------------------------------------

# Each user gets a section.  To start a section, put the username in
# brackets on a line by itself.  To set something for that user, specify
# it under that section heading.  The username is case-sensitive, so
# admin and AdMiN are two different users.
#
# Possible settings:
#
# password: The user's password.  This is case-sensitive.
#
# --------------------------------------------------------------------------
#
# actions: Let the user do certain things with upsd.  
# 
# Valid actions are:
#
# SET	- change the value of certain variables in the UPS
# FSD   - set the "forced shutdown" flag in the UPS
# 
# --------------------------------------------------------------------------
#
# instcmds: Let the user initiate specific instant commands.  Use "ALL"
# to grant all commands automatically.  There are many possible  
# commands, so use 'upscmd -l' to see what your hardware supports.  Here
# are a few examples:
#
# test.panel.start	- Start a front panel test
# test.battery.start	- Start battery test
# test.battery.stop	- Stop battery test
# calibrate.start	- Start calibration
# calibrate.stop	- Stop calibration
#
# --------------------------------------------------------------------------
#
# Example:
#
#	[admin]
#		password = mypass
#		actions = SET
#		instcmds = ALL
#

#
# --- Configuring for a user who can execute tests only
#
#	[testuser]
#		password  = pass
#		instcmds  = test.battery.start
#		instcmds  = test.battery.stop

#
# --- Configuring for upsmon
#
# To add a user for your upsmon, use this example:
#
#	[upsmon]
#		password  = pass
#		upsmon master
# or
#		upsmon slave
#
# The matching MONITOR line in your upsmon.conf would look like this:
#
# MONITOR myups@localhost 1 upsmon pass master	(or slave)

Ubuntu 22.04.3 sur portable et 23.10 sur fixe

Hors ligne

#34 Le 18/01/2016, à 18:23

jnq

Re : désinstallation paquet ipp-linux impossible

upsdeamon non configuré :

# Network UPS Tools: example upsmon configuration
#
# This file contains passwords, so keep it secure.

# --------------------------------------------------------------------------
# RUN_AS_USER <userid>
#
# By default, upsmon splits into two processes.  One stays as root and
# waits to run the SHUTDOWNCMD.  The other one switches to another userid
# and does everything else.
#
# The default nonprivileged user is set at compile-time with
# 	'configure --with-user=...'.  
# 
# You can override it with '-u <user>' when starting upsmon, or just
# define it here for convenience.
#
# Note: if you plan to use the reload feature, this file (upsmon.conf)
# must be readable by this user!  Since it contains passwords, DO NOT
# make it world-readable.  Also, do not make it writable by the upsmon
# user, since it creates an opportunity for an attack by changing the
# SHUTDOWNCMD to something malicious.
#
# For best results, you should create a new normal user like "nutmon",
# and make it a member of a "nut" group or similar.  Then specify it
# here and grant read access to the upsmon.conf for that group.
#
# This user should not have write access to upsmon.conf.
#
# RUN_AS_USER nut

# --------------------------------------------------------------------------
# MONITOR <system> <powervalue> <username> <password> ("master"|"slave")
#
# List systems you want to monitor.  Not all of these may supply power
# to the system running upsmon, but if you want to watch it, it has to
# be in this section.
# 
# You must have at least one of these declared.
#
# <system> is a UPS identifier in the form <upsname>@<hostname>[:<port>]
# like ups@localhost, su700@mybox, etc.
# 
# Examples:
# 
#  - "su700@mybox" means a UPS called "su700" on a system called "mybox"
#
#  - "fenton@bigbox:5678" is a UPS called "fenton" on a system called
#    "bigbox" which runs upsd on port "5678".
#
# The UPS names like "su700" and "fenton" are set in your ups.conf
# in [brackets] which identify a section for a particular driver.
#
# If the ups.conf on host "doghouse" has a section called "snoopy", the
# identifier for it would be "snoopy@doghouse".
#
# <powervalue> is an integer - the number of power supplies that this UPS 
# feeds on this system.  Most computers only have one power supply, so this 
# is normally set to 1.  You need a pretty big or special box to have any 
# other value here.
#
# You can also set this to 0 for a system that doesn't supply any power,
# but you still want to monitor.  Use this when you want to hear about
# changes for a given UPS without shutting down when it goes critical,
# unless <powervalue> is 0.
#
# <username> and <password> must match an entry in that system's
# upsd.users.  If your username is "monmaster" and your password is 
# "blah", the upsd.users would look like this:
#
#	[monmaster]
#		password  = blah
#		upsmon master 	(or slave)
# 
# "master" means this system will shutdown last, allowing the slaves
# time to shutdown first.
#
# "slave" means this system shuts down immediately when power goes critical.
#
# Examples: 
#
# MONITOR myups@bigserver 1 monmaster blah master
# MONITOR su700@server.example.com 1 upsmon secretpass slave
# MONITOR myups@localhost 1 upsmon pass master	(or slave)

# --------------------------------------------------------------------------
# MINSUPPLIES <num>
#
# Give the number of power supplies that must be receiving power to keep
# this system running.  Most systems have one power supply, so you would
# put "1" in this field.
#
# Large/expensive server type systems usually have more, and can run with
# a few missing.  The HP NetServer LH4 can run with 2 out of 4, for example,
# so you'd set that to 2.  The idea is to keep the box running as long
# as possible, right?
#
# Obviously you have to put the redundant supplies on different UPS circuits
# for this to make sense!  See big-servers.txt in the docs subdirectory
# for more information and ideas on how to use this feature.

MINSUPPLIES 1

# --------------------------------------------------------------------------
# SHUTDOWNCMD "<command>"
#
# upsmon runs this command when the system needs to be brought down.
#
# This should work just about everywhere ... if it doesn't, well, change it.

SHUTDOWNCMD "/sbin/shutdown -h +0"

# --------------------------------------------------------------------------
# NOTIFYCMD <command>
#
# upsmon calls this to send messages when things happen
#
# This command is called with the full text of the message as one argument.
# The environment string NOTIFYTYPE will contain the type string of
# whatever caused this event to happen.
#
# Note that this is only called for NOTIFY events that have EXEC set with
# NOTIFYFLAG.  See NOTIFYFLAG below for more details.
#
# Making this some sort of shell script might not be a bad idea.  For more
# information and ideas, see docs/scheduling.txt
#
# Example:
# NOTIFYCMD /bin/notifyme

# --------------------------------------------------------------------------
# POLLFREQ <n> 
#
# Polling frequency for normal activities, measured in seconds.
#
# Adjust this to keep upsmon from flooding your network, but don't make 
# it too high or it may miss certain short-lived power events.

POLLFREQ 5

# --------------------------------------------------------------------------
# POLLFREQALERT <n>
#
# Polling frequency in seconds while UPS on battery.
#
# You can make this number lower than POLLFREQ, which will make updates
# faster when any UPS is running on battery.  This is a good way to tune 
# network load if you have a lot of these things running.  
#
# The default is 5 seconds for both this and POLLFREQ.

POLLFREQALERT 5

# --------------------------------------------------------------------------
# HOSTSYNC - How long upsmon will wait before giving up on another upsmon
#
# The master upsmon process uses this number when waiting for slaves to
# disconnect once it has set the forced shutdown (FSD) flag.  If they
# don't disconnect after this many seconds, it goes on without them.
#
# Similarly, upsmon slave processes wait up to this interval for the 
# master upsmon to set FSD when a UPS they are monitoring goes critical -
# that is, on battery and low battery.  If the master doesn't do its job,
# the slaves will shut down anyway to avoid damage to the file systems.
#
# This "wait for FSD" is done to avoid races where the status changes
# to critical and back between polls by the master.

HOSTSYNC 15

# --------------------------------------------------------------------------
# DEADTIME - Interval to wait before declaring a stale ups "dead"
#
# upsmon requires a UPS to provide status information every few seconds
# (see POLLFREQ and POLLFREQALERT) to keep things updated.  If the status
# fetch fails, the UPS is marked stale.  If it stays stale for more than
# DEADTIME seconds, the UPS is marked dead.
#
# A dead UPS that was last known to be on battery is assumed to have gone
# to a low battery condition.  This may force a shutdown if it is providing
# a critical amount of power to your system.
#
# Note: DEADTIME should be a multiple of POLLFREQ and POLLFREQALERT.
# Otherwise you'll have "dead" UPSes simply because upsmon isn't polling
# them quickly enough.  Rule of thumb: take the larger of the two
# POLLFREQ values, and multiply by 3.

DEADTIME 15

# --------------------------------------------------------------------------
# POWERDOWNFLAG - Flag file for forcing UPS shutdown on the master system
#
# upsmon will create a file with this name in master mode when it's time
# to shut down the load.  You should check for this file's existence in
# your shutdown scripts and run 'upsdrvctl shutdown' if it exists.
#
# See the shutdown.txt file in the docs subdirectory for more information.

POWERDOWNFLAG /etc/killpower

# --------------------------------------------------------------------------
# NOTIFYMSG - change messages sent by upsmon when certain events occur
#
# You can change the default messages to something else if you like.
#
# NOTIFYMSG <notify type> "message"
#
# NOTIFYMSG ONLINE	"UPS %s on line power"
# NOTIFYMSG ONBATT	"UPS %s on battery"
# NOTIFYMSG LOWBATT	"UPS %s battery is low"
# NOTIFYMSG FSD		"UPS %s: forced shutdown in progress"
# NOTIFYMSG COMMOK	"Communications with UPS %s established"
# NOTIFYMSG COMMBAD	"Communications with UPS %s lost"
# NOTIFYMSG SHUTDOWN	"Auto logout and shutdown proceeding"
# NOTIFYMSG REPLBATT	"UPS %s battery needs to be replaced"
# NOTIFYMSG NOCOMM	"UPS %s is unavailable"
# NOTIFYMSG NOPARENT	"upsmon parent process died - shutdown impossible"
#
# Note that %s is replaced with the identifier of the UPS in question.
#
# Possible values for <notify type>:
#
# ONLINE   : UPS is back online
# ONBATT   : UPS is on battery
# LOWBATT  : UPS has a low battery (if also on battery, it's "critical")
# FSD      : UPS is being shutdown by the master (FSD = "Forced Shutdown")
# COMMOK   : Communications established with the UPS
# COMMBAD  : Communications lost to the UPS
# SHUTDOWN : The system is being shutdown
# REPLBATT : The UPS battery is bad and needs to be replaced
# NOCOMM   : A UPS is unavailable (can't be contacted for monitoring)
# NOPARENT : The process that shuts down the system has died (shutdown impossible)

# --------------------------------------------------------------------------
# NOTIFYFLAG - change behavior of upsmon when NOTIFY events occur
#
# By default, upsmon sends walls (global messages to all logged in users)
# and writes to the syslog when things happen.  You can change this.
#
# NOTIFYFLAG <notify type> <flag>[+<flag>][+<flag>] ...
#
# NOTIFYFLAG ONLINE	SYSLOG+WALL
# NOTIFYFLAG ONBATT	SYSLOG+WALL
# NOTIFYFLAG LOWBATT	SYSLOG+WALL
# NOTIFYFLAG FSD	SYSLOG+WALL
# NOTIFYFLAG COMMOK	SYSLOG+WALL
# NOTIFYFLAG COMMBAD	SYSLOG+WALL
# NOTIFYFLAG SHUTDOWN	SYSLOG+WALL
# NOTIFYFLAG REPLBATT	SYSLOG+WALL
# NOTIFYFLAG NOCOMM	SYSLOG+WALL
# NOTIFYFLAG NOPARENT	SYSLOG+WALL
#
# Possible values for the flags:
#
# SYSLOG - Write the message in the syslog 
# WALL   - Write the message to all users on the system
# EXEC   - Execute NOTIFYCMD (see above) with the message
# IGNORE - Don't do anything
#
# If you use IGNORE, don't use any other flags on the same line.

# --------------------------------------------------------------------------
# RBWARNTIME - replace battery warning time in seconds
#
# upsmon will normally warn you about a battery that needs to be replaced
# every 43200 seconds, which is 12 hours.  It does this by triggering a
# NOTIFY_REPLBATT which is then handled by the usual notify structure
# you've defined above.
# 
# If this number is not to your liking, override it here.

RBWARNTIME 43200

# --------------------------------------------------------------------------
# NOCOMMWARNTIME - no communications warning time in seconds
#
# upsmon will let you know through the usual notify system if it can't
# talk to any of the UPS entries that are defined in this file.  It will
# trigger a NOTIFY_NOCOMM by default every 300 seconds unless you 
# change the interval with this directive.

NOCOMMWARNTIME 300

# --------------------------------------------------------------------------
# FINALDELAY - last sleep interval before shutting down the system
#
# On a master, upsmon will wait this long after sending the NOTIFY_SHUTDOWN
# before executing your SHUTDOWNCMD.  If you need to do something in between
# those events, increase this number.  Remember, at this point your UPS is 
# almost depleted, so don't make this too high.
#
# Alternatively, you can set this very low so you don't wait around when
# it's time to shut down.  Some UPSes don't give much warning for low
# battery and will require a value of 0 here for a safe shutdown.
#
# Note: If FINALDELAY on the slave is greater than HOSTSYNC on the master,
# the master will give up waiting for the slave to disconnect.

FINALDELAY 5

# --------------------------------------------------------------------------
# CERTPATH - path to certificates (database directory or directory with CA's)
#
# When compiled with SSL support, you can enter the certificate path here.
#
# With NSS:
# Certificates are stored in a dedicated database (splitted in 3 files).
# Specify the path of the database directory.
# 
# CERTPATH /etc/nut/cert/upsmon
#
# With OpenSSL:
# Directory containing CA certificates in PEM format, used to verify
# the server certificate presented by the upsd server. The files each
# contain one CA certificate. The files are looked up by the CA subject
# name hash value, which must hence be available.
#
# CERTPATH /usr/ssl/certs
# 
# See 'docs/security.txt' or the Security chapter of NUT user manual
# for more information on the SSL support in NUT.

# --------------------------------------------------------------------------
# CERTIDENT - self certificate name and database password
# CERTIDENT <certificate name> <database password>
#
# When compiled with SSL support with NSS, you can specify the certificate
# name to retrieve from database to authenticate itself and the password
# required to access certificate related private key.
#
# CERTIDENT "my nut monitor" "MyPasSw0rD"
# 
# See 'docs/security.txt' or the Security chapter of NUT user manual
# for more information on the SSL support in NUT.

# --------------------------------------------------------------------------
# CERTHOST - security properties for an host
# CERTHOST <hostname> <certificate name> <certverify> <forcessl>
#
# When compiled with SSL support with NSS, you can specify security directive
# for each server you can contact.
# Each entry maps server name with the expected certificate name and flags
# indicating if the server certificate is verified and if the connection
# must be secure.
#
# CERTHOST localhost "My nut server" 1 1
#
# See 'docs/security.txt' or the Security chapter of NUT user manual
# for more information on the SSL support in NUT.

# --------------------------------------------------------------------------
# CERTVERIFY - make upsmon verify all connections with certificates
# CERTVERIFY 1
#
# When compiled with SSL support, make upsmon verify all connections with 
# certificates.
# Without this, there is no guarantee that the upsd is the right host.
# Enabling this greatly reduces the risk of man in the middle attacks.
# This effectively forces the use of SSL, so don't use this unless
# all of your upsd hosts are ready for SSL and have their certificates
# in order.
# When compiled with NSS support of SSL, can be overriden for host 
# specified with a CERTHOST directive.


# --------------------------------------------------------------------------
# FORCESSL - force upsmon to use SSL
# FORCESSL 1
#
# When compiled with SSL, specify that a secured connection must be used
# to communicate with upsd.
# If you don't use 'CERTVERIFY 1', then this will at least make sure
# that nobody can sniff your sessions without a large effort.  Setting
# this will make upsmon drop connections if the remote upsd doesn't
# support SSL, so don't use it unless all of them have it running.
# When compiled with NSS support of SSL, can be overriden for host 
# specified with a CERTHOST directive.

Ubuntu 22.04.3 sur portable et 23.10 sur fixe

Hors ligne

#35 Le 18/01/2016, à 18:39

nany

Re : désinstallation paquet ipp-linux impossible

jnq a écrit :

upsd.conf non configuré

Voilà pour l’alimenter :

sudo bash -c 'echo -e "\nLISTEN 127.0.0.1 3493\nLISTEN ::1 3493" >> /etc/nut/upsd.conf'

À ce stade, tu dois pouvoir commencer à voir des résultats :
Par exemple :

sudo upsd
sudo upsc MGE-UPS@localhost ups.status

Pour avoir la liste complète :

sudo upsc MGE-UPS@localhost

Je reviens pour les autres fichiers.

En ligne

#36 Le 18/01/2016, à 19:03

jnq

Re : désinstallation paquet ipp-linux impossible

Bonsoir super ça marche !

sudo upsd
Network UPS Tools upsd 2.7.1
fopen /var/run/nut/upsd.pid: No such file or directory
listening on ::1 port 3493
listening on 127.0.0.1 port 3493
Connected to UPS [MGE-UPS]: usbhid-ups-MGE-UPS
sudo upsc MGE-UPS@localhost ups.status
Init SSL without certificate database
OL CHRG
sudo upsc MGE-UPS@localhost
Init SSL without certificate database
battery.charge: 100
battery.charge.low: 20
battery.runtime: 1875
battery.type: PbAc
device.mfr: EATON
device.model: Protection Station 800
device.serial: AN2E49008
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.7.1
driver.version.data: MGE HID 1.32
driver.version.internal: 0.38
input.transfer.high: 264
input.transfer.low: 184
outlet.1.desc: PowerShare Outlet 1
outlet.1.id: 2
outlet.1.status: on
outlet.1.switchable: no
outlet.2.desc: PowerShare Outlet 2
outlet.2.id: 3
outlet.2.status: on
outlet.2.switchable: no
outlet.desc: Main Outlet
outlet.id: 1
outlet.power: 25
outlet.switchable: no
output.frequency.nominal: 50
output.voltage: 230.0
output.voltage.nominal: 230
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.firmware: 1.13
ups.load: 10
ups.mfr: EATON
ups.model: Protection Station 800
ups.power.nominal: 800
ups.productid: ffff
ups.serial: AN2E49008
ups.status: OL CHRG
ups.timer.shutdown: 0
ups.timer.start: 0
ups.vendorid: 0463

Par contre l'indicateur graphique dans la barre de menu disparaît toujours et impossible a faire revenir. Sauf en redémarrant le pc. Il disparait juste apres la commande de démmarage sudo upsdrvctl start

Dernière modification par jnq (Le 18/01/2016, à 19:06)


Ubuntu 22.04.3 sur portable et 23.10 sur fixe

Hors ligne

#37 Le 18/01/2016, à 19:10

nany

Re : désinstallation paquet ipp-linux impossible

jnq a écrit :

upsd user non configuré

Voilà pour lui :

sudo bash -c 'echo -e "\n[admin]" >> /etc/nut/upsd.users'
sudo bash -c 'echo -e "    password = adminpass" >> /etc/nut/upsd.users'
sudo bash -c 'echo -e "    actions = SET" >> /etc/nut/upsd.users'
sudo bash -c 'echo -e "    instcmds = ALL" >> /etc/nut/upsd.users'
sudo bash -c 'echo -e "\n[upsmonitor]" >> /etc/nut/upsd.users'
sudo bash -c 'echo -e "    password  = userpass" >> /etc/nut/upsd.users'
sudo bash -c 'echo -e "    upsmon master" >> /etc/nut/upsd.users'

Puis édite le fichier en root pour modifier (par ce que tu veux comme mots de passe) adminpass et userpass sachant que ce qui va remplacer userpass va servir dans le fichier suivant.

En ligne

#38 Le 18/01/2016, à 19:15

nany

Re : désinstallation paquet ipp-linux impossible

jnq a écrit :

Par contre l'indicateur graphique dans la barre de menu disparaît toujours et impossible a faire revenir. Sauf en redémarrant le pc. Il disparait juste apres la commande de démmarage sudo upsdrvctl start

Je pense que c’est normal.
Ça changera peut-être lorsque que le dernier fichier sera configuré. Sinon, peut-être que l’icône n’est censée apparaître qu’en mode batterie.

En ligne

#39 Le 18/01/2016, à 19:46

nany

Re : désinstallation paquet ipp-linux impossible

jnq a écrit :

upsdeamon non configuré

Et voilà :

sudo sed -i '85a\MONITOR MGE-UPS@localhost 1 upsmonitor userpass master\n' /etc/nut/upsmon.conf

Puis tu édites le fichier en root pour remplacer (à la ligne 85) userpass par le mot de passe que tu auras mis pour upsmonitor dans le fichier précédent.

En ligne

#40 Le 18/01/2016, à 19:58

nany

Re : désinstallation paquet ipp-linux impossible

Liste non exhaustive de ce qui m’a permis de te guider en plus de la page de doc :

Dernière modification par nany (Le 18/01/2016, à 19:58)

En ligne

#41 Le 18/01/2016, à 20:13

jnq

Re : désinstallation paquet ipp-linux impossible

Tous les fichiers sont configurés. Grand test. NUT monitor installé. Démarrage automatisé. Merci pour les liens de documentation j'ai de la lecture pour un moment.
L'icône rouge de la barre de menu disparaît toujours. Dommage.
Encore merci pour ton aide et ta patience.

Dernière modification par jnq (Le 18/01/2016, à 20:36)